Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, In P1001 you can set direct speed in RPM at which you want to run the motor, set p1016 = 2, set signal source of DI BI of PB. So that you can run the motor at fixed set point. Please refer attached sheet for more information. AttachmentG120C_fixed set pt.pdf (372 Downloads) |
This contribution was helpful to2 thankful Users |
3/8/2018 8:52 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello, With what you have made a commissioning with BOP-2, iOP, starter, startdrive? https://inverterdrive.com/file/Siemens-Sinamics-G120C-Getting-Started Please have a look this FAQ to connect the Sinamics to HMI: https://support.industry.siemens.com/cs/ww/en/view/109481157 https://support.industry.siemens.com/cs/ww/en/view/97550333
|
Last edited by: Ste39 at: 3/8/2018 8:54:44 PMLast edited by: Ste39 at: 3/8/2018 8:57:42 PMLast edited by: Jen_Moderator at: 3/12/2018 12:22:37 PMOptimized links. |
|
3/9/2018 11:57 AM | |
Posts: 7 Rating: (0) |
I use BOP-2 for commissioning,300 parameters for motor are ok, for fixed speed I use P1000=3 P1001= 500 P1016= 2 P1020=1 P1021=0 P1022=0 P1023=0 P1070=500 Now I see on the inverter that RDY is blinking green, I connect terminal 5 (DI0) with terminal 9 (24V Out) , it is strange that BF is blinking red, I even do not use a Profibus, I made a total reset by P010=3 (parameter reset) and 970=1 but still can`t run it. Any other ideas sir ? thanks |