11/21/2018 6:33 AM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
Dear Pioneros, As what I know, you could not work around with the error with a real CPU. If you test it in PLC Sim environment, you can work around with it. Simulate the error 1. Set up plc sim with your project. Download the project. 2. Add few blocks, record down the instance DB number. 3. Download changes into PLC sim, half way of it, press cancel. 4. Then the error similar to your cases should happen. Solve the error 5. Then you could go to ONLINE block folder, delete the DB that have partially downloaded into PLC SIM. 6. Initiate the download changes again. 7. This round should be successful. However, the only issue is, you are not able to add Copy/paste/Delete your offline instance DB to Running/Stopped S7 400 CPU Online Block Folder. (i tested in CPU410-5H). If not, you have no way but to do a full download on the PLC. Hope it helps. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
11/21/2018 11:44 AM | |
Joined: 3/29/2017 Last visit: 7/23/2024 Posts: 16 Rating: (0) |
Solved the problem without full loading. Opened "Blocks" online. Removed those db which was not offline. |
11/22/2018 1:33 AM | |
Joined: 9/9/2015 Last visit: 9/15/2024 Posts: 727 Rating: (278) |
Dear Pioneros, Removing a faceplate graphics in WinCC does not affect the program in the PLC, it only affects the WinCC Runtime. Great to hear that you have solved the issues. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
11/22/2018 10:02 AM | |
Joined: 3/29/2017 Last visit: 7/23/2024 Posts: 16 Rating: (0) |
Thanks for the help |
Follow us on