10/7/2015 3:08 PM | |
Posts: 439 Rating: (108) |
Hello, I had to configure and download the new software controller CPU1507S last week and had hard time figuring how to do it. I always got the same "hardware mismatch" when I tried to download into the software PLC from my programming station. So, I did a procedure to do it for me to remember, to give to my customer and for people on Siemens website who are looking for a simple procedure. There is missing information in the manual of the software controller about configuring one port to be the port to download the PC configuration and the other port to be the PLC port. I suppose there will be application example and more detailed manual in the future, so it will be easier to figure how to do it. If you have further question, don't hesitate. Best regards, Hugo AttachmentS7-1500 CPU1507S Software controller procedure.pdf (1693 Downloads) |
Last edited by: HugoD at: 10/7/2015 3:12:08 PMLast edited by: HugoD at: 10/7/2015 3:23:45 PMLast edited by: HugoD at: 10/7/2015 3:26:32 PM |
This contribution was helpful to13 thankful Users |
12/14/2018 6:25 PM | |
Hello MatLcq, This is a good idea for test purpose but for the end industrial application it would be nice to set the firewall correctly. You will find more information about the port Siemens use in the STEP7 Professional manual. SIMATIC STEP 7 Basic/Professional V15.1 and SIMATIC WinCC V15.1 Section 2.1 Security information. Port 102 : S7 communication Communication to the S7 controller via Ethernet/PROFINET for programming Have a good one! Best regards, HugoD Attachment2.1 Security information.pdf (808 Downloads) |
This contribution was helpful to1 thankful Users |