4/23/2019 1:00 PM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hello wantutri, the group displays in the overview area provides the plant operator with an overview of the status of the entire plant in process mode. You assemble the messages of the group displays from the lower-level process pictures that belong to this area. The group displays in the overview area are always displayed. The group displays in the overview area are displayed by default. This does not require configuration. So why do you generate the block icons and hide them behind an other object in WinCC? So the group displays at the navigation part should working and in Runtime you can't see or use the block icon. With regards |
This contribution was helpful to1 thankful Users |
4/24/2019 5:03 PM | |
Joined: 2/1/2010 Last visit: 9/19/2024 Posts: 150 Rating: (71) |
wantutri The following suggestion is certainly not a best practice, but it should fit your use case: Have you considered just manually placing some group display objects from the library on your .pdl file which are manually configured to the event states for the objects in CFC (e.g. MonDiL)? You will need to customize the appearance (bit position, dimensions, etc) according to your needs. You can hide or not hide those group displays during runtime, either way the hierarchy roll up will catch them. |
If my post helped you, please rate. Thanks. |
|
This contribution was helpful to1 thankful Users |