10/14/2019 1:41 PM | |
Joined: 7/9/2015 Last visit: 9/25/2024 Posts: 3945 Rating: (586)
|
Hi, I found some informations about LED in the fully compatible successor product ES7151-1AA06-0AB0 Please check manual on page 37 for remedy - SF "not relevant" and BF flashing.... SIMATIC Dezentrale Peripherie ET 200S Interfacemodul IM151-1 STANDARD (6ES7151-1AA06-0AB0)Regards, Towome |
|
|
10/14/2019 2:09 PM | |
Joined: 1/18/2017 Last visit: 2/29/2024 Posts: 54 Rating: (1) |
If you're referring to this, please see answers below in bold: The interface module is not configured or is configured incorrectly. No data exchange is taking place between the DP master and the interface module. Causes: • The PROFIBUS address is incorrect. • Parameter assignment error • Parameter assignment error Remedy: • Check the interface module. Module was replaced and HW downloaded • Check the configuration and parameter assignment. What needs to be done here? • Check the PROFIBUS address. Profibus address is the same in HWConfig and on IM |