5/22/2014 1:43 PM | ||||||||||||||||||||||
Joined: 4/19/2008 Last visit: 9/3/2024 Posts: 1525 Rating: (159) |
Hello Krrish, To implement you need to have a IM which is cable to save the Event Recording 6ES7 153-2BA02-0XB0 & DI Module Which is 6ES7 326 1BK01 0AB0, Have a Look on the Application Example Here Buffering of Process Messages including Time Stamps with ALARM_7B |
|||||||||||||||||||||
Ammy |
||||||||||||||||||||||
This contribution was helpful to1 thankful Users |
5/22/2014 2:43 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello Krrish !! For resolution of 100ms you don't need any fancy hardware. Assuming that the basic cycle time of your plc is generally 10-20ms these days, a SOE program can be created in STEP7 which detects thechanges in stats of of Signals required to be monitored and stores them in a SOE DB along with the time stamp. You could create a DB with say 50-100 events ( even more if needed ). Every time a new event occurs, the oldest event ispushed out. We have done this several times with accuracy of 10-20mswithout any issues. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
5/22/2014 4:53 PM | ||||||||||||||||||||||
Joined: 11/8/2011 Last visit: 8/21/2024 Posts: 387 Rating: (43) |
Add on software i dont think its required. Have look on the How does the time-stamp function work in the ET200M, and what should you watch out for during configuration? event recording thread hope it will help |
|||||||||||||||||||||
Last edited by: Saggy at: 5/22/2014 4:53 PM |
||||||||||||||||||||||
This contribution was helpful to2 thankful Users |
4/3/2018 6:28 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by TheCloverTech is split to a separate thread with the subject Time stamping for binary signals with 10 ms resolution. Best regards |