9/19/2014 1:11 PM | |
Posts: 28 Rating: (0) |
Hi I have had trouble downloading the standard block FC105 for scaling an analog input PIW288. It puts the CPU in error and gives me several different reasons as to why the block is corrupt. All other code in the block is ok as I can download the function block as long as I delete the FC105 network. I have included the program and hardware set up in an attatchment. Thanks in advance
Attachmentcpu_312 fc105 fault.pdf (437 Downloads) |
9/19/2014 1:15 PM | |
Joined: 8/27/2010 Last visit: 4/13/2024 Posts: 417 Rating: (37) |
Can u please attach diagnostics buffer event? In my opinion you just forget to download FC105 itself to the CPU. |
9/19/2014 1:36 PM | |
Posts: 28 Rating: (0) |
HI Here is the buffer and fault message. Attachmentcpu_312 fc105 fault.pdf (383 Downloads) |
9/20/2014 9:52 AM | |
Posts: 28 Rating: (0) |
Tried to download FC105 and it wont go? Screen shot in attatchment. Starting to think the cpu type will not accept it?? Thanks AttachmentFC105 fault.pdf (322 Downloads) |
9/20/2014 11:43 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, If you look at the technical details of i.e. this CPU, You can see that you can load Max 64 FC's. The blocknumber of the FC you want to load may not be higher then 64 . That's why you need to renumber FC105. Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to1 thankful Users |