6/10/2015 8:46 PM | |
Posts: 1 Rating: (0) |
SINAMICS G120 POWER MODULE PM240-2 does this need fuses on the incoming cables? I was looking through the manual and it shows that it has a fused slot and gives the recommend fuses for this application? ---------------------------------------------------------------------------------------------------- Split from Overload and over current in Sinamics G120. |
Last edited by: Min_Moderator at: 6/11/2015 2:12:36 PMNew subject after splitting |
|
6/15/2015 2:02 PM | |
Joined: 10/11/2006 Last visit: 4/26/2024 Posts: 5825 Rating: (789)
|
Hello, additional line fuses are necessary.
4.1 Installation conditions +
5.1.2 Connection overview for PM240-2 https://support.industry.siemens.com/cs/ww/en/view/109474573
|
With best regards, |
|
6/20/2018 12:18 PM | |
Joined: 8/21/2014 Last visit: 4/3/2024 Posts: 139 Rating: (1) |
Hi, If I am using multiple PM240-2 drives(with cu110 controller) do I need to connect fuse for each drive? If I am having 6 modules. Do I need to fix (6*3 = 18 fuses or Circut Breakers ) ? I cant able to access the below link!
|
6/20/2018 12:31 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Yes, you need to provide separate/individual protection to power module. For more details please refer SINAMICS Power Modules, Protective Devices for Power Modules PM240-2 link. Please refer attached sheet for detail information about PM power connections. HTH. AttachmentPM240 2 power module connection circuit.pdf (190 Downloads) |
Last edited by: PISCEAN 2010 at: 6/20/2018 12:45:01 PMLast edited by: Jen_Moderator at: 6/21/2018 8:34:02 AMOptimized link. |
|