(4)| 10/27/2015 7:49 PM | |
|
Posts: 439 Rating:
|
Vulpes, Here is the S7-1200 manual for the wiring of the CM1241, see page 1265.
Not used for RS485: Output
Best regards, Hugo |
| 10/27/2015 7:56 PM | |
|
Posts: 439 Rating:
|
Here |
| 10/28/2015 2:27 PM | |
|
Posts: 439 Rating:
|
vulpes, You can find a zipped library attach to the post where you will find the UDT I created, DB3 and OB1. Best regards, Hugo AttachmentModbus RTU library.zip (1443 Downloads) |
This contribution was helpful to
|
|
| 10/28/2015 2:33 PM | |
|
Posts: 439 Rating:
|
vulpes, Here is the whole PLC Modbus slave. Best regards, Hugo AttachmentModbus RTU slave.zip (2079 Downloads) |
This contribution was helpful to
|
|