Hello Mikhail Feoktistov, I need your help , I have sinamics g120 drive with control unit CU 240E-2 PN , one of the drive got fault now i want to replace the control unit , I colone parameters from the running drive from another similar machine using BOP 2 but the problem is drive is showing Conn Error. The IP address, ID and subnet mask is not configuring, but when I install that control unit from which i colone parameters, machines start working properly. Kindly guide me step by step to configure IP address and subnet mask to my new control unit. The procedure which i followed was, 1- Factory reset 2- Transfer parameter from bop to drive 3- Then I changed P8920 to 114 following parameters from running drive and P8921 index 0: 192, index 1: 168, index 2: 0 and index 3: 3 4- same thing with P8922 5- Enter subnet mask in P8923 as index 0: 255, index 1: 255 index 2: 255 and Index 3: 0 Then I changed P8925 to 2 and power off drive when i power on drive the still sowing Bus Fault LED blinking also the IP address, ID and subnet mask not showing in R8931,R8930 and R8933
Is the way I did is rite ? kindly guide step by step the rite way Thank you ------------------------------------------------------------------------------------------ |