12/13/2016 9:38 AM | |
Posts: 72 Rating: (1) |
Hello, Do you know what is the structure of Siemens Telegram 390 and what should be write in Control Word to be able to run the DCM? Regards, Adam |
2/20/2020 1:33 PM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating: (300) |
Hi Adask, the structure of Telegram 390 you find in the list manual here: https://support.industry.siemens.com/cs/ww/en/view/109763564 See chapter 3.6, page 729 for the overview and page 748 and following for detailed bit structure. The telegram 390 is just to communicate to the Control Unit part of DCM (e.g. reading the status of the digital inputs). To run the drive you need to communicate to the drive part with another telegram, e.g. telegram 1, 3, 352,... with those telegrams you can switch on the drive and give the speed setpoint etc. Depending on your application there are also ready to use PLC function blocks, e.g. for speed control with telegram 1 -> for SIMATIC there is the SINA_SPEED block available in the driveLib. |
Last edited by: RB91 at: 02/20/2020 13:37:15Best regards, |
|