Hello! I'm having trouble loading my webserver program to the PLC. the program is just a marker, and webserver enabled from CPU properties. when i download the program, there is a warning that says: manual synchronization required. and the option to synchronize is unavailable, if i click continue without synchronization, the program can't be downloaded to the PLC. PLC: 6ES7 212-1BE40-0XB0 router: LB-link ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 6/23/2017 2:31:56 PMNew subject after splitting |
|
6/23/2017 7:08 PM | |
Joined: 7/7/2010 Last visit: 11/19/2024 Posts: 15406 Rating: (2446)
|
I recall having a difficult time updating a web server's DBs. Seems I had closed the web page without properly exiting / logging out. The PLC still had an active web connection established, orphaned by clicking the X.... and would not allow me to update the web server. I restarted the PLC and it allowed me to download.
|
science guy |
|