(2)| 8/18/2017 10:03 AM | |
|
Joined: 7/9/2015 Last visit: 12/17/2025 Posts: 4493 Rating:
|
Hi, in Step 7 TIA V14 it´s possible to simulate a communication with PUT/GET but only over integrated interface of PLC - not over CPs. Check the following FAQ: How do you simulate communication between two CPU modules?Regards, Towome |
|
|
|
| 8/21/2017 9:19 AM | |
|
Posts: 1368 Rating:
|
Hello, which version of PLCSim you use? Look at Chapter 7.2 of the PLCSIM V14 manual to see, which plc could communicate each others. https://support.industry.siemens.com/cs/ww/de/view/109741755 |
| 8/21/2017 9:45 AM | |
|
Posts: 5 Rating:
|
Hi, I'm using TIA Portal V13.0 with S7-PLCSIM V5.4+SP5+Upd 3. Best regards Kattus |
| 8/21/2017 10:29 AM | |
|
Joined: 10/7/2005 Last visit: 12/19/2025 Posts: 3052 Rating:
|
Hello kattus a physical S7-300 requires usage of FB14/15 GET/PUT blocks which are though NOT supported by PLCSIM. The trick is program your S7-300 as if it is an S7-400 and directly use SFB14/15 GET/PUT blocks and it will work (just make sure to change the program back to use of FB14/15 when you want to use it in a physical S7-300). |
|
Cheers |
|
This contribution was helpful to
|
|
| 8/21/2017 11:02 AM | |
|
Posts: 5 Rating:
|
Hi fritz, It worked perfect. Thank you very much. Have a nice day :D Kattus |
This contribution was helpful to
|
|
| 8/24/2017 12:20 PM | |
|
Posts: 8171 Rating:
|
New question published by vuvinh11 is split to a separate thread with the subject What should configure in program when call FB14/FB15 and to use as SFB14/15?. Best regards |
Follow us on