10/27/2019 5:57 PM | |
Joined: 9/27/2006 Last visit: 9/26/2024 Posts: 12283 Rating: (2685) |
Hello Hebeshe; Analog inputs that are used for temperature (RTD, TC) are scaled by 10.0. You could do the scaling (from Word to Real) in the PLC (or simply make the value a Real, 259.0, and divide it by 10.0, to show 25.9): https://support.industry.siemens.com/cs/us/en/view/77316903 Or in WinCC, divide the resulting value by 10.0, so you have a result that shows a decimal. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/27/2019 17:59:27 |
|
10/27/2019 6:03 PM | |
Posts: 12 Rating: (0) |
Hello, thanks for your fast response. How can I divide the value by 10 ?? when I using the linear scaling function , the out value became only (25) not (25.9) |
10/27/2019 6:20 PM | |
Posts: 12 Rating: (0) |
DB20.DB0 is int when i make trend using it it only show integers values, no float point . |
Last edited by: Hebeshe at: 10/27/2019 18:23:06 |
|
10/27/2019 6:24 PM | |
Posts: 12 Rating: (0) |
the PLC program is old program and I only working in the HMI, |