5/25/2020 1:33 PM | |
Joined: 10/22/2019 Last visit: 5/23/2024 Posts: 45 Rating: (0) |
|
5/25/2020 1:37 PM | |
Joined: 10/22/2019 Last visit: 5/23/2024 Posts: 45 Rating: (0) |
Maybe word 3 and 4 are not for current or torque? |
5/25/2020 1:41 PM | |
Joined: 10/22/2019 Last visit: 5/23/2024 Posts: 45 Rating: (0) |
i dont receive nothing on word 3 4 5 6.why is that? |
5/25/2020 3:11 PM | |
Joined: 9/16/2008 Last visit: 9/18/2024 Posts: 57 Rating: (3) |
The drive parameter p922 needs to be set to telegram 352 also - |
5/25/2020 10:14 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
I asume, you have selected Telegram 1 in Devices&Networks for the drive. If you use STARTER you have to configurate Tel 352 in Starter too. If you use Startdrive this is done automatically. If you made the changes in th drive online use "RAM to ROM". If you made it offline save and download it into the drive. Make a power off and on cycle with the drive. Now it should work. Selecting the Tel 352 in STARTER or Startdrive will set automatically the BiCo settings in the drive to transmit the current, torque, fault and warning via PROFINET or PROFIBUS. This may help you too: https://support.industry.siemens.com/cs/ww/en/view/78788716 |
Last edited by: miami at: 05/25/2020 22:24:11 |
|
Follow us on