Apologies if this is the wrong forum for this but it is the only one I have found other questions on UPS1600. I have setup a supply as follows: PSU8200 (20A) connected to a UPS1600, this is then connected to a 5Ah UPS1100 battery. On the UPS I have linked out terminals 9 and 10. I have connected terms 11 and 12 to the battery X2 terms and obviously connected BAT terms between UPS and battery. I cannot get the battery to charge, I have a battery ok LED that comes and goes on the battery but through the SITOP CD UPS manager diagnostics I can see that battery is at 0V and also charging current is zero, I have a not ready to buffer alarm Anybody have any ideas on why this is happening? is there an initial activation you have to do to set the battery to charge? Thanks |
9/2/2020 4:11 PM | |
Joined: 7/15/2008 Last visit: 1/21/2025 Posts: 382 Rating: (44) |
Hello, Did you open the cover of the UPS Battery and check if the batteries are connected. The module usually ships with the battery leads disconnected. Regards / m.f.g |