6/17/2019 9:51 AM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33823 Rating: (4203)
Do you use an additional expansion modul AM2 or an analog input on the basic modul? |
6/17/2019 9:53 AM | |
Joined: 11/21/2016 Last visit: 8/14/2023 Posts: 9 Rating: (0) |
Yes i am using the AM2 |
6/17/2019 10:09 AM | |
In the appendix a possible solution. Since at 4-20 mA and a display range of 0 - 2000 l, the gain of the signal requires a gain with 3 decimal places, I use 2 analog amplifiers connected in series. Since I do not know if and how many analog inputs are enabled on the base module, I have assigned the analog input the address 1 (AI1). Attachmenttank_capacity_0BA8.Standard.zip (331 Downloads) |
6/17/2019 10:35 AM | |
Thanks a lot. I will have it tested later today |
6/17/2019 3:01 PM | |
Sorry my pressure transmitter is 0 to 1 bar.What do the scaling need to be then? |
6/17/2019 3:03 PM | |
The same. You want to display the tank capacity, not the pressure. |
6/17/2019 4:04 PM | |
Here is the tanks layout on the attachment. I hope it will help
Attachment07284_00-Layout1.pdf (369 Downloads) |