Hello, It seems, you have 2 problems. 1. Wrong motor protection, because your motor burned. Choose a right motor protection. https://www.electrical4u.com/motor-protection-relay-for-high-voltage-induction-motor/ 2. Blocked motor or too much load, because to high current could be the reason for your issue. |
With best regards, |
|
This contribution was helpful to1 thankful Users |
7/18/2018 5:58 PM | |
Posts: 241 Rating: (1) |
do u know the position of actuator when starting this large fan? i mean it must be close or open? and what about after starting? |
7/19/2018 12:22 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, your accrual protection doesn't protect the motor. You have no star/delta or soft starter or inverter to reduce the inrush current. You should think about such a solution, to implement a functioning motor protection. https://support.industry.siemens.com/cs/ww/en/view/21384967 It seems, the deviation between the inrush current and rated current is so big, that thermal overload relay with rated current would trigger during run up. Your only device to reduce the current is the dumper. So when during run up the damper is not closed, it has no effect. So you can check this, too. |
With best regards, |
|
This contribution was helpful to2 thankful Users |
7/20/2018 3:17 PM | |
Posts: 241 Rating: (1) |
that motor starting method was star_delta |