2/11/2016 9:04 PM | |||||||||||||||||||||||||||||
Joined: 3/28/2015 Last visit: 2/24/2021 Posts: 641 Rating:
|
Hello, Perhaps the following topic might help:
Restore memory card with S7-1500
|
||||||||||||||||||||||||||||
Eng.Mohamed Ibrahim |
|||||||||||||||||||||||||||||
2/12/2016 12:06 PM | |
Joined: 2/18/2013 Last visit: 8/31/2017 Posts: 102 Rating:
|
You could downgrade the firmware again and try if it works: https://support.industry.siemens.com/cs/ch/de/view/92274475 |
This contribution was helpful to
1 thankful Users |
2/12/2016 4:37 PM | |
Joined: 9/23/2014 Last visit: 2/18/2021 Posts: 42 Rating:
|
That ended up working, thanks. I did some testing, and the card is only compatible with firmware version 1.7. Versions 1.8.1-1.8.3 all give me the same error. Very strange.
|
2/12/2016 5:26 PM | |
Joined: 2/18/2013 Last visit: 8/31/2017 Posts: 102 Rating:
|
Maybe you just discovered a compatibility problem between 1.7 and 1.8.x. If you would contact Siemens the problem could be analyzed in detail. Of course they would need your memory card content. But it seems you need to stick to 1.7 or migrate to 1.8.x via a new download into the PLC. Before the download I would recommend to delete all project data from the memory card or maybe to format the memory card. This should work without a need to recompile the project. However your configuration would still contain a V1.7 PLC. I assume this step would repair your memory card problem. Alternatively or in a second step you may consider changing the configured PLC from 1.7 to 1.8 then recompile and then download so that you would be able to use new features of V1.8.x.
|