7/15/2011 11:36 AM | |
Posts: 39 Rating: (0) |
Hello. I am using a booksize 100 Kw (6SL3130-1TE31-0AA0) in a machine. THis infeed is configued on SIMOTION D 435 with version 4.1 Sinamics Integrated verison PN2.2 DP 2.6.2. Fault 30062 ( THe bypass contactor was opened under current) has occured on the infeed. THis particular error does not get reset and ever after a complete power off this error does not get acknowledged. This is the second instance, where this particular fault has occured!!! As per the logic, we are giving the EP when the 3 phase is supplied to the panel, then the main contactor is picked up and then the ON command is given to the infeed. This procedure is always followed in a sequence. Are there any probable reasons as to why this fault occurs and I have come across some news saying this fault gets acknowledged in HF11 of V2.6.2 Sinamics. Since my infeed is on the SIMOTION which version of SINAMICS Integrated has this HF? And what can be done do reduce the occurance of this error. Please help Reagrds. AttachmentLMW Machine Infeed_F30062.zip (395 Downloads) |
Last edited by: PPM__ at: 7/15/2011 2:53 PMLast edited by: PPM__ at: 7/15/2011 12:46 PM |
|
This contribution was helpful to1 thankful Users |
2/1/2012 7:57 PM | |
Posts: 31 Rating: (1) |
Hello, I have the same error message F30062 on a Cu320, how did you solve your problem? Thanks |
This contribution was helpful to1 thankful Users |
2/29/2012 4:48 PM | |
Joined: 3/2/2007 Last visit: 10/16/2024 Posts: 938 Rating: (5) |
hy sirs , did anyone solve this problem ? thank you |
... thank you ... |
|
7/8/2021 5:48 AM | |
Joined: 12/28/2016 Last visit: 10/7/2024 Posts: 435 Rating: (50) |
Hi You need to update the firmware. Updates to versions higher than 4.4 may prevent AOP from communicating with CU. S120 Firmware Version 4.4 |