1/23/2017 8:37 AM | |
Joined: 7/9/2015 Last visit: 4/24/2024 Posts: 3812 Rating: (554) |
Hi, please check manual on page 33. There you can read abou flashing of you LED: the output circuit is overloaded: --> Voltage dip, automatic voltage recovery, Voltage drop, reduction of service life https://support.industry.siemens.com/cs/de/en/view/8859629 Regards, Towome |
1/23/2017 9:02 AM | |
Posts: 6 Rating: (0) |
All right, it is the LED green 'OK' that ignites then goes out as if the food(supply) 220v disappeared, while it is always present. |
1/23/2017 9:17 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1050) |
hi, what does it mean, "it freezes in the cabinet"? regards, |
FCK WAR! |
1/23/2017 9:31 AM | |
-8° Celsius in the electrical cabinet . (armoire électrique) . |
1/23/2017 9:43 AM | |
this can be a problem, if you don´t have SIPLUS-modules. the climatic environmental conditions of S7-300 modules are from 0-60° Celsius. Have a look in this manual, chapter 11.4: SIMATIC S7-300 CPU 31xC and CPU 31x: Installation hope this helps, regards, |
FCK WAR! |
1/23/2017 10:07 AM | |
It is good of what I thought, thank you for your help. |