7/12/2013 1:28 AM | |
Joined: 6/14/2013 Last visit: 3/18/2023 Posts: 218 Rating: (9) |
good day, look on the side of manual s7-300, Chapter 6 |
7/12/2013 3:48 AM | |
Posts: 139 Rating: (5) |
Hello, Normally, transducer is 2 wire connection (Loop power ) and in that case please check your Module Jumper (i think D mode) in hardware and in software module configuration you have to select 2DMU for this. If this is still in testing phase, then disable Channel Diagnostics and Test it out. please check attach for 2 wire and 4 wire connection. Attachment6ES7331-7NF10-0AB0.pdf (396 Downloads) |
Last edited by: C.kt at: 7/12/2013 3:52 AM |
|
7/12/2013 5:27 AM | |
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating: (9) |
Check the wiring again, sometimes its loose wiring that is the cause of problem. . |
7/12/2013 5:47 AM | |
Posts: 1064 Rating: (72) |
Check you plug on th eside and verify the setting |
7/12/2013 10:08 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi Ayzetina, It is good practice to disable the unused channels. |
7/12/2013 4:08 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi Ayzetina, Send us your connections and hardware configuration. |
7/12/2013 4:38 PM | |
Posts: 14 Rating: (0) |
Hello, attached you will find the connections that I have, also the configuration for this project. Thanks for your help.
Attachmentimages.zip (269 Downloads) |
7/12/2013 5:11 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi Ayzetina, Did you try to disconnect a wire from the channel and put an ammeter in series? The current flows? |
7/12/2013 5:17 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi |
7/12/2013 5:21 PM | |
Posts: 14 Rating: (0) |
Yes I've already check the bus connectors and they're ok, even I try with different connectors, but that didn't solve the problem. Thanks for answering
|