Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello BigJohn; That part number appears to correspond to your requirements, thanks. Now the issue is: why does the RS-485 connectivity not seem to work with the ABB master? Standard connectivity on RS-485 networks usually supports the standard 3-8 +5GND sequence. And electrical levels are very different on RS-232 and RS-485. If you look at the following table you will see that for RS-232 comms you would be expected to use pins 2-3. This is from the 7SJ8 manual, that you can download from this page: The problem is that Siprotec is not a Siemens Automation product (the division that supports this forum is Siemens IA&D), but a product developed and marketed by the Siemens Energy division. And yes, they do not talk to each other very well. So I am not even sure that this can be answered by a Support request from the forum. MikeJ, a member here who works for the Energy division and who is kind enough to share his experience with us, has provided a link to the Energy divison support line. I suggest you use it to contact them about this issue. See the following thread for example. https://support.industry.siemens.com/tf/ww/en/posts/85660/ Remember that using communication pins at larger than expected voltage levels can destroy the communication electronics, so be careful with your tests in the meantime. Hope this helps, Daniel Chartier |
This contribution was helpful to2 thankful Users |
3/9/2016 7:20 AM | |
Joined: 11/7/2012 Last visit: 8/28/2023 Posts: 67 Rating: (0) |
Dear Mike, Thanks for usful answer. I can manage to put it back on RS485. Thanks |