Hello Dhavalvadhel: What is exactly the designation of your flowmeter, E&H dos not show a model by that name. If you actually have a Proline Promag W HART model, you can setup the analog output as a 4-20 mA signal representing ONE active value (without using HART functions), as you can see in the screenshot below,m taken from this E&H manual: https://portal.endress.com/wa001/dla/5000523/1581/000/05/BA01063DEN_0617.pdf If this is not your model of flowmeter, search fpr the exact designation on the E&H website, it provides a great deal of useful information on its instruments. The analog input in your ET 200SP should be wired as a 4-wire connection, since power for the analog output is provided by the flowmeter (an active signal). https://support.industry.siemens.com/cs/ww/en/view/109475183 Hope this helps, Daniel Chartier |