Hi, You can do this on the "MeasPP" block. Set "PV_AH_Lim" to 140.0 and set the delay time for that limit to 600seconds. |
Last edited by: Oreca at: 3/4/2016 11:27:20 AMIf I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |
3/18/2016 11:54 AM | |
Joined: 3/14/2008 Last visit: 9/20/2024 Posts: 2095 Rating: (936) |
When selection tags, you have several options at the upper left corner: ES tags, through OS server PC name, S7 program. Please select a few options in order to get the AS program hierarchy, where you can select the TAG. Also, why don't you use the create block icon option? |
If I could help you, you can use the RATE button. Thank you. |
|
3/18/2016 12:18 PM | |
Joined: 3/14/2008 Last visit: 9/20/2024 Posts: 2095 Rating: (936) |
Hi AlwintGru, You scare me a bit with your undergoing problems.. -> Cannot use the ES to configure your OS project, problems with redundancy and download issues...PCS7 can be a real pain in the ass when there is a problem with your installation or setup/configuration. I hope you will get your project running smoothly. What is your complete setup like? ES, OS servers, clients?, Overview of your multiproject. Communication plant bus/terminal bus etc. Are you using clients as well? You can use one server, just turn off the standby server. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
3/22/2016 4:59 PM | |
Joined: 3/14/2008 Last visit: 9/20/2024 Posts: 2095 Rating: (936) |
Hi AlwintGru aka AgrS, Glad that the issue is solved! Before, I wanted to suggest that maybe you send the project so I could take a look at, rather then guessing most time what the issue could be (works better if you have the project at your disposal), but knew that Siemens was coming to you. Good luck with the rest! |