11/9/2010 6:26 PM | |
Posts: 1 Rating: (0) |
I got another problem with PAC3100. I have a installation of 16 nos. of devices in one location. Suddenly all the energy counters of all devices were frozen. When I restart them that issue was solved. Again after 2 months I got the same issue in all 16 Nos. only energy counters were frozen and all other readings were ok. I'm using PAC Modbus RTU integration with RXC00U+PXA30RS1 and I didn't see any issue with that Modbus side also. Please reply. Splitted from SENTRON PAC 3100 Problem. |
Last edited by: O_Moderator at: 11/11/2010 10:38 AMnew subject after splitting |
|
12/2/2010 4:08 PM | |
Posts: 3 Rating: (0) |
Hello, You need update your Firmware to PAC 3100 In the Attment you will find the instruction Firmware Update SENTRON PAC 3100 Firmware update V1.0.1 incorporates the following modifications: After a longer period of operation (> 1 month), the built-in energy counters may stop counting. They might start to work again after some time, or in case of a power loss. This malfunction may lead in a rising deviation between the measured energy, and the real energy consumption. Version V1.0.1 eliminates this behavior.It is recommended to update all devices with prior versions to the version V1.0.1 in order to ensure that the energy counters are working properly. ! Requires installation of a language package version V1.0.x or higher ! Link Firmware : http://support.automation.siemens.com/WW/view/en/46392580 Link: Language Package http://support.automation.siemens.com/WW/view/en/46393010 AttachmentInstruction - Firmware Update SENTRON PAC3100_en.pdf (561 Downloads) |
Last edited by: peres at: 12/2/2010 4:39 PMLast edited by: peres at: 12/2/2010 4:36 PM |
|
12/19/2010 9:29 PM | |
Posts: 50 Rating: (6)
|
Hello, Is your energy counter frozen displayed value problem solved, or do you have further problems after the device firmware update to V1.0.1? |
Follow us on