7/10/2013 5:38 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hi 10leiva, Send us your hardware configuration. |
7/10/2013 6:10 PM | |
Joined: 7/3/2013 Last visit: 2/15/2023 Posts: 11 Rating: (0) |
the analog inputs are in the hardware config4.jpg
AttachmentHardware config1.zip (385 Downloads) |
7/10/2013 6:49 PM | |
Joined: 4/19/2008 Last visit: 9/3/2024 Posts: 1525 Rating: (159) |
Hello 10leiva, Have a look on the Wiring Detail on the Manual, have you done the wiring same way? 2AI I 2WIRE ST analog electronic module (6ES7134-4GB01-0AB0) |
Ammy |
|
7/10/2013 7:48 PM | |
Joined: 7/3/2013 Last visit: 2/15/2023 Posts: 11 Rating: (0) |
Yes. "+" to "1" and "-" to "2", (IW2000). "+" to "5" and "-" to "6", (IW2002).
|
7/10/2013 8:23 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Attach a screen shot where the AI is reading and scaling. |
7/11/2013 7:42 AM | |
Joined: 4/17/2012 Last visit: 8/30/2024 Posts: 474 Rating: (10) |
Hi, Just check this block
Attachmentfor_ref.zip (242 Downloads) |
7/11/2013 3:20 PM | |
Joined: 7/3/2013 Last visit: 2/15/2023 Posts: 11 Rating: (0) |
In the manual (page 7), the wirin detail indicates channel 1 at terminals 1 and 2 (at left) and channel 2 at terminals 5 and 6 (right) is it. .? May be different module type came in my mind. . Sorry to misguide you. . If wiring is ok and mA also came as per actual. . Then try one thing. . Re defined process Image Input Area (e.g. 512) then assign address less than your PII area and then check your counts. . YESSS. That is the solution. you solved my problem for the second time this month. ThanksPranav J. Bhagat
|
This contribution was helpful to1 thankful Users |