3/8/2017 10:05 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
Here is a small example with two levels. This will show you the way. The resolution is 0.4 ° C. Attachmentthermocouple.zip (493 Downloads) |
This contribution was helpful to2 thankful Users |
3/10/2017 8:51 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
No. |
3/10/2017 8:56 AM | |
Posts: 32 Rating: (0) |
tip in boiling water the A/D output voltage was 1.343 VDC. in condition described above, is the A/D working properly or not? |
3/10/2017 10:07 AM | |
Posts: 32 Rating: (0) |
thermocouple type:K transmitter:ENDA model name:ECTC-LV i made these settings: 1:input: K 2:scale min: 1(minum measurement scale=0) 3:scale: 5(measurement scale=400) 4:output: 0-10V transmitter datasheet attached AttachmentECTC-UV ENDA.pdf (252 Downloads) |
3/10/2017 12:27 PM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
Is it absolutely certain that the thermocouple is type K? |
3/10/2017 12:59 PM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
Sorry, then I do not know how I can still help you. |
3/15/2017 8:56 PM | |
Joined: 3/27/2009 Last visit: 2/11/2024 Posts: 92 Rating: (6) |
I use PR 4110 from prelectronics |
3/16/2017 12:03 PM | |
Posts: 56 Rating: (3) |
How mV for thermocouple. Without converter. 100 st.C = 4.095 mV. |
3/17/2017 8:39 PM | |
Posts: 32 Rating: (0) |
by using a precision multimeter you can measure thermocouple output mV. 4.096 mV for 100 degree celsius from the omega k type mv table. Attachmentz204-206.pdf (363 Downloads) |
Last edited by: sx50 at: 3/17/2017 8:40:38 PM |
|