8/17/2015 2:40 PM | |
Posts: 116 Rating: (2) |
what do you mean with " can it be that there was alway a IP was set? " |
8/17/2015 4:32 PM | |
Posts: 116 Rating: (2) |
Hi Christoph, Here is a result. 1_xx : they connect laptop to Siemens switch (one port connect to Siemens HMI, one port to X120 of D435) 2_xx: they connect directly to X120 of D435 Nothing reply at all? AttachmentProneta.zip (251 Downloads) |
Last edited by: Tikki at: 8/17/2015 4:34:08 PM |
|
8/17/2015 4:55 PM | |
Posts: 116 Rating: (2) |
I believe they did connect to Simotion controller. But I doubt with result. do I need to consider cross cable with direct connect to D435? |
8/17/2015 5:43 PM | |
Posts: 116 Rating: (2) |
Christoph, We got 8 !!! at 7-segment display |
8/17/2015 6:11 PM | |
Posts: 116 Rating: (2) |
So, 8 and 8. (8 dot) without middle segment flicker is same then ? How to fixed it? |
8/17/2015 6:13 PM | |
Posts: 116 Rating: (2) |
shall I try this ? from your previous answer What's happen if you put the PLC switch to stop and powerON? |
8/17/2015 6:40 PM | |
Posts: 116 Rating: (2) |
Very sorry, It my mistake, fan is there |
8/17/2015 6:44 PM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011)
|
Hi, ok then you should check if the SIMOTION works longer if is not switched to state RUN. Regards |
8/17/2015 7:26 PM | |
Posts: 116 Rating: (2) |
Here after put PLC switch to stop, power off and power on -> they got all LED red and 7-segment remain in state 8. What do you think? HW failure ? |
8/17/2015 7:43 PM | |
Posts: 116 Rating: (2) |
Hey, funny thing.. if you make zoom in they did it wrong. I asking them to do it again. Sorry |
8/17/2015 7:54 PM | |
Posts: 116 Rating: (2) |
I hope so, Thanks a lot for your support. |