6/28/2013 9:00 AM | |
Posts: 81 Rating: (2) |
Hello, I am getting some strange problems in AO(332-5HF00-0AB0) modules. When i am giving setpoint to AO module via scaling logic, it not getting value in mA at terminal side. My scaling logic is L 50.0 L 1.000000e+002 /R L 2.764800e+004 *R RND T QW 512 I have done setting at AO termical as current source from 4-20 mA please find attachment. reagrds, manoj AttachmentAO.pdf (248 Downloads) |
Last edited by: CS Moderator at: 6/29/2013 3:50 PMnew subject after splitting from /tf/WW/en/Posts/30111#top |
|
6/28/2013 9:28 AM | |
Posts: 559 Rating: (87) |
Try it out with FC106 Unscale block. Also use PQW 512 instead of QW512. |
6/29/2013 8:49 AM | |
Posts: 72 Rating: (2) |
hi I think modul is not a probleam. how you are measure ma? kindly check your wiring.
|
Last edited by: Murali Rajendran at: 6/29/2013 8:50 AM |
|
6/30/2013 11:27 AM | |
Posts: 559 Rating: (87) |
Yes there is no problem in Logic. The problem must be somewhere at your hardware side. Please check it out or change the channel address & then check. |
8/8/2013 8:07 AM | |
Posts: 81 Rating: (2) |
Hello, I am measuring mA on multimeter. I am direclt forcing value in QW. But still it is not genrating any kind of value on my multmeter. Is my settings are correct with this module?? Dear experts plz resolve this issue as soon as possible. regards, manoj
AttachmentAO.pdf (181 Downloads) |
8/8/2013 8:30 AM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hi MANOJ.N, In which terminals are you measuring the current? Send us a diagram of your connections on the board. |
8/8/2013 8:51 AM | |
Posts: 81 Rating: (2) |
Hello from this diagram,I am getting confused. On which terminal I have to measure current?? regards, manoj
|
8/8/2013 9:02 AM | |
Posts: 81 Rating: (2) |
Hello, Yes i am measring current on the same terminal 3 for +ve & 6 for -ve terminal. regards, manoj
|
8/8/2013 10:25 AM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hi MANOJ.N, You have applied a load of this measurement? |
8/8/2013 11:32 AM | |
Posts: 81 Rating: (2) |
Hello, I have not applied any load to module. I am just checking mA value on AO module. Regards, manoj
|
8/8/2013 11:53 AM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hi MANOJ.N, Try to put a load to the terminals, you will have a tool to 4-20 ma and put the ammeter in series. |