10/10/2012 4:15 PM | |
Posts: 836 Rating: (100)
|
Looks good for you (depending on the description given). Check out documentation: SIMATIC Process Control System PCS7 PCS 7 Advanced Process Library V8.0 Chapter 1.1.10.28 / page 132: - Feature Bit 15 (description on page 139): Neutral position manipulated variable takes effect with "out of service" operating mode You can use this Feature bit to specify if the block should go to the neutral position when ittransitions to the "Out of service" operating mode. Default position is "0". Bit = 0: The block does not go to the neutral position at the transition to the "out of service" operating mode. Bit = 1: The block goes to the neutral position at the transition to the "out of service" operating mode. Refer to the Neutral position for motors, valves and controllers (Page 37) section for more information. |
This contribution was helpful to1 thankful Users |
10/11/2012 4:19 PM | |
Posts: 836 Rating: (100)
|
Won't you get a error due to descrepancy of the valves CTRL output and the wrong feedback? |