5/7/2020 10:08 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello Tomact; I have not worked with a CM As-i master ST yet, but I have done projects with other As-i masters (on the S7-300 and other manufacturers' PLCs ) and DP-As-i Links in the past. This "wrong type" or "incorrect slave type" message is common enough, and is generally related to a configuration error or mismatch between the expected slave and actual slave. Your CER (configuration error) LED should be active when this diagnostic message appears. Explanations can be found in chapter 8 of the CM As-i master ST manual (see the screenshot below): https://support.industry.siemens.com/cs/ww/en/view/71756485: Note that this error message will appear only if you configure the parameters of the As-i master to signal them, look at parameters in the same manual. If you are confident that the slaves selected and configured are correct and you do not feel this message is warranted, you can set the system so it does not show "Wrong Type". Hope this helps, Daniel Chartier |
5/7/2020 10:08 PM | |
Joined: 9/21/2012 Last visit: 9/23/2024 Posts: 4161 Rating: (464) |
Do you have a Topology defined for the AS-i network? Did you try to re-scan the AS-i network? |