Hello JohVer; The As 410-5H CPU system manual shows that for a redundant configuration you can use the same racks as you would for any H-system PLC. See the attachment below. Fail-safe operation does not imply a change of rack; see the section that discusses Fail-safe operation in the manual. CPU 410-5H Process Automation - Industry Support SiemensHave you given a thought to the type of system expansion card (P.O. license) you wll be installing in your new AS 410-5H? The operation of a CPU 410-5H requires a system expansion card. The system expansion card specifies the maximum number of process objects that can be loaded to the CPU and saves the license information in case of a system expansion. The system expansion card forms a hardware unit with the CPU 410-5H. See this link from the Siemens Industry Mall (Electronic Catalog): https://mall.industry.siemens.com/mall/en/ww/Catalog/Search/?searchTerm=CPU%20410-5H&tab=Product Go to the lower part of the webpage, where the system expansion cards are described; play around with the configurator available there; for example: SIMATIC PCS 7CPU410-5HBUNDLE PO 2K+,CPU410-5HPROCESS AUTOMATION FOR S7-400 AND S7-400H/F/FH, WITH SYSTEM EXPANSION CARD MORE THAN 2000 PROCESS OBJECTS Note: The 2000 P.O. license is the largest you can purchase, it basically means "unlimited". Hope this helps, Daniel Chartier |