Joined: 12/28/2016 Last visit: 9/13/2024 Posts: 434 Rating: (45) |
I also encountered the same problem(I can not chenge p0010 ) but I could not connect to the inverter with Starter software. I want to upload the drive parameters but I can not ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 2/28/2019 2:12:09 PMNew subject after splitting https://pnap.ir |
|
3/1/2019 8:40 AM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, in Starter search for the accessible nodes, you can find this button at the top-middle of your Starter screen. Then you can accept the found device and it will be imported automatically to your project. Then go online and start the upload. If your starter cannot detect the devices fw version, you have to install the correct SSP for your device. If you need further assistance you can contact the technical support: https://support.industry.siemens.com/my/ww/en/requests#createRequest |
With best regards, |
|