I have this problem exactly in my Project. i can't modify any Input/output addresses, only Memory/DB address possible to modify. i havn't any Block with Know-How Protect. in TIA V14 was possibled to modify everything(I/O/M Address). ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/29/2019 13:56:54New subject after splitting |
|
8/29/2019 4:14 PM | |
Joined: 7/7/2010 Last visit: 9/20/2024 Posts: 15211 Rating: (2417)
|
Where are you attempting to alter the address? You can open the PLC tag table and "rewire" tags to a different input or output. You can open the hardware device and expand the right half of the working pane see and change the input and output addresses used by each hardware module. You can right-click and rewire tags in the logic and change what the I/O address is for a given tag. What changed that makes you want to alter I/O addresses?
|
science guy |
|