Hello. There is CPU319-3 PN / DP (6ES7318-3EL00-0AB0), digital Input SM 326 F-DI 24x24V DC (6ES7326-1BK02-0AB0) and digital output SM322 DO 16XDC24V / 0.5A. The equipment configuration was collected in SIMATIC Manager. After the power supply is supplied to the modules and loading the configuration in the CPU, the SF LED is lit on the SM 326 module, and the CPU is in the RUN mode.(The DIP switch on the SM 326 module is set to the address 8). Can the SM326 module connect to CPU319-3 PN / DP? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/22/2021 10:34:37New subject after splitting |
|
6/28/2021 8:15 AM | |
Joined: 7/5/2017 Last visit: 8/12/2024 Posts: 8 Rating: (0) |
AttachmentDiagnose.txt (424 Downloads) |
Last edited by: Andrej_88 at: 06/28/2021 08:16:19Last edited by: Andrej_88 at: 06/28/2021 08:17:40 |
|
7/7/2021 2:59 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi Andrej_88, I guess this manual is what you searching about: SIMATIC Industrial Software S7 Distributed Safety - configuring and programmingIn safety-mode the F-addresses are only allowed to be written from the F-programm of its runtime-group. hope this helps, regards, |