Industry Online Support
Technical Forum
11/29/2009 7:57 AM | |
Joined: 5/28/2008 Last visit: 9/9/2024 Posts: 4515 Rating: (839)
|
Dear nnnvvvttt, First of all, You have to select a drive with power equal to the motor power. You can select also drive with power greater than the motor power. But not less than it. Thus because, the power modules inside the drive carring the full current of the motor. So, if you selected a drive with power 11kW for instance to drive a motor of 22kW, It will damage or tripped. There's many families in MM4. Please read the following tip to know the difference between them. Difference between Micromaster 411, 420, 430 & 440 After selecting the suitable Micromaster family, you have to identify if you want the drive with internal filter, or not. I recommend as you are a student to select drive without a filter to minimize the cost. Then you can reach to the drive part number. Regards, |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
11/29/2009 2:46 PM | |
Posts: 3 Rating: (0) |
What you let me know is really useful! Thank you very much! |
Last edited by: nnnvvvttt at: 11/29/2009 2:58 PM |
|