7/18/2014 4:42 PM | |
Joined: 10/10/2010 Last visit: 9/14/2024 Posts: 307 Rating: (15) |
almost transducers are DC voltage or cuurent or resistor ( RTD pt100) |
8/18/2014 9:17 AM | |
Joined: 8/27/2010 Last visit: 4/13/2024 Posts: 417 Rating: (37) |
Hi! 1. Previously, you specified order number asS3-VD-3-05A4B, rather thenS3-VD-3-05A40. When you specify 0 in order code (option) that means you order transducer with some optional meausring range and supply voltage. I do not know, which option you choose when you ordered tansducer. I think some label/sticker shpuld present on device with specification data. Otherwise - contact your supplier/manufacturer. 2. 17.5 mA looks in correct range. However, if your device have a measuring range of 0..500V, at 500 V device should have exactly 20 mA output current. Again, I do not know which range you specified in your order code option. 3. Compatibility issue can present in case you do not know exact output range. 4. Diagram looks fiine. 5. Again, please provide exact order number with ALL options I asked. 6. You can use variable table to monitor the input of analog module. Just create VAT (where your program blocks is located), type your AI adress inside and monitor the value there. Usethismanual, page 441 for a guide. |