Hello, take a look in capter 3.3 of the commissioning manual S120. Each motor module is a Drive Object in the CU320-2. For each Drive Object you can configure a seperat telegram slot in the communication overwiew of the SINAMICS S120 in starter. after the configuration transfer the telegramms to hwconfig with starter and then you have a I/O Slot for each MotorModule in you PLC adress space. Regards Christoph |