3/8/2012 9:23 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Can you please specify what exactly you want? |
3/8/2012 11:58 AM | |
Posts: 2 Rating: (0) |
hi PISCEAN 2010 I want control (CUD1&CUD2) all digital Input&Output bitsof drive 6RA70 with profibus. but i can not . |
Last edited by: PLCM at: 3/9/2012 6:52 AM |
|
3/9/2012 9:35 AM | |
Joined: 8/25/2006 Last visit: 4/19/2024 Posts: 2203 Rating: (277) |
Hello. Look at function diagram sheets Z110, G110, G111 and G112 of the manual. To send the status of digital inputs to the PLC you may, for example, connect the K0020 (status of DI) to the parameter U734.05 (look at Z110). Thus you will see in the PLC the status of DI in the fifth word of the DP telegram. Description of K0020 is on page 652. To control the DO of drive send the control word in the DP telegram from PLC to the drive. E.g. it will be the fifth word also. Then use binectors B3500-B3515 (Z110)and connect them in parameters P771 - P774 (look at G112). |