Hi, it is not exactly clear what you are asking. If you wish to know HOW the Control and Status words are connected to the outside world (not to each other as your question implies) then you first need to ascertain which method of connection is used. There are several, Digital, USS, Profibus, Simolink etc. You need to look in theCompendium(I have used VC for simplicity), and look in the "Basic Function Diagram" section Basically, there are 2 main function diagrams that can start you in the right direction. See FD180 (Control Word 1) and 200 (Status Word 1). You can then determine what controls the drive, and how the drive reports its status back to the upper controller For example, what is parameter P554.1 (What starts and Stops the drive) set to, if it is in the range 2xxx.x, then its Serial, or if it is 3xxx.x, then its profibus, or 10 - 22, then its digital etc, but use Function Diagram 180 to find this out. Regards, Graeme
|