1/12/2015 12:58 PM | |
Posts: 467 Rating: (59)
|
hello, it is not possible to convert DC-1 or DC-3 to DC-13 rating.Because the DC-13 has according IEC 60947-4-1 other switching condition as the DC-1 or DC-3/DC-5 utilization category. kind regards LesPaul |
This contribution was helpful to1 thankful Users |
2/1/2015 2:27 PM | |
Posts: 16 Rating: (0) |
Hi dear LesPaul AttachmentContactor-Overload U Series-1.pdf (266 Downloads) |
2/11/2015 9:51 AM | |
Posts: 467 Rating: (59)
|
hello,
The 3RT contactor are tested according DC-1,DC-3, DC-5 and the 3RH type are tested according DC-13.
If you want a DC-13 rating for a main contactor you should start a service request at the Hotline ( mail: technical–assistance@siemens.com) with a
description of your application. So the colleagues can forward the inquiry to the laboratory. kind regards LesPaul |