May be this might be an issue. Netpro / HW monitored in some other system at the same time. |
8/27/2015 9:15 PM | |
Joined: 1/15/2009 Last visit: 4/19/2024 Posts: 316 Rating: (40)
|
Hi Cermatic, It sounds like there is a service running that makes the station think there is another online connection when there may not be (i have seen this when some one went online with a Block, or CFC, HW Config, Netpro..etc). I would first try a shutdown of the Engineering Station. Give it a few minutes, then start up again, and re-try. If this fails, check to see if you can do a changes CFC download succesfully or if you get a similar message. Then if that fails, try contacting Technical Support https://support.industry.siemens.com/tf/ww/en/header/supportrequest/ |
The best location for all PCS 7 content (manuals, guides, application notes, FAQs, and videos). |
|
This contribution was helpful to1 thankful Users |
5/23/2016 8:33 AM | |
Joined: 11/16/2012 Last visit: 3/22/2024 Posts: 227 Rating: (31) |
Hi everyone, this error message also appears if there is a online connection from a second PG/PC. How to check the PG communication see the following FAQ (only german at the moment): Regards |