4/23/2019 5:22 PM | |
Joined: 8/24/2010 Last visit: 7/10/2024 Posts: 30 Rating: (1) |
Hi Christoph, The order code is 6ES7 416-5HS06-0AB0 and the firmware used is V6.0. Thanks, |
4/26/2019 7:32 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hello monkeyjacob, in the FAQ Where do you find the latest firmware for S7-41x CPUs? you can find for every CPU-Typ the download entry for the firmware. With regards |
4/29/2019 8:20 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hello monkeyjacob, another reason for the error can be that some system functions can insert direct in a runtime group. So probably the problem can be solved, if you build a block around the SFC12. A good manual for writing your own block is the S7-SCL manual. With regards |
6/4/2019 9:45 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hello, by chance I came across the answer to the post today. Unfortunately, the H-CPU does not support SFC functions 11 and 12. See the manual SIMATIC Fault-tolerant systems S7-400H in the sections Differences between fault-tolerant systems and standard systems. So if you want to deactivate a DP Slave you have to use the a single CPU (without H) or you can use the CPU 410 with the firmware V8.2 or higher. In stand-alone operation the CPU 410 (Single AS), individual DP stations or PN devices can now be activated or deactivated on PROFBUS and PROFINET by means of the system function D_ACT_DP (SFC 12). This function is not available in case of a redundant configuration. With regards |
This contribution was helpful to1 thankful Users |
6/4/2019 2:33 PM | |
Joined: 8/24/2010 Last visit: 7/10/2024 Posts: 30 Rating: (1) |
Hi Heisenberg, I thank you a lot for your answer! It was very helpful and interesting. Monkeyjacob |
Follow us on