Hello Sipti; The part number of the analog module you mention corresponds to a ET 200SP system, so it appears you are connecting your CPU 319F to this module through Profibus or Profinet. On these fieldbuses it is possible to remove a complete station from the polling list of the CPU (not a single module, mind you, a complete station including the IM module and all I/O modules) using the SFC 12 "D_ACT_DP": Disconnect DP slaves by means of SFC12 Enabling a disabled DP slave with SFC 12 'D_ACT_DP' https://support.industry.siemens.com/cs/ww/en/view/19730984 If this could be a solution to your problem (having this "optional" module as the sole module on a ET 200SP station, for example) it would be possible to deactivate/re-activate it through SFC 12). Hope this helps, Daniel Chartier |