Hi, Well, we have a project with blocks: CH_AI (FC275) with author CHN71 and CPU_RT (FB128) with author DRIVER81. If though it is not desired and unwanted, it works... I think the update from PCS7 V5.2 to V7.1 did not went OK. Did you update from V5.2->V6.0->V6.1->V7.0->V7.1? (what I mean is updating in steps). The block CPU_RT for example is created automatically if you have a CPU that supports this block. It is created automatically with the driver from your current PCS7 version. I suggest you will update the driver blocks from 5.2 to the 7.1. You have to copy the blocks from the PCS7 library V7.1 to your project and update block types. I think you will need to do a full download of the PLC. Have you seen this manual? |
Last edited by: Oreca at: 05/01/2019 10:03:56If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
5/10/2019 9:10 AM | |
Joined: 3/14/2008 Last visit: 9/23/2024 Posts: 2096 Rating: (936)
|
Hi MicroMan Glad it is solved!! |