5/11/2015 8:53 PM | |
Joined: 9/27/2006 Last visit: 4/18/2024 Posts: 12256 Rating: (2664) |
Hello Luigi; For some reason your original post was garbled, it is easier to readf in the quote section below.
Ok , in the manuals, if there are things that can help, but if you follow the manual but did not get the expected result or in the manual says to do.
As for my question , maybe not explain it well , what I need is the following things :
1. - I have a PLC , it has in its network of PROFIBUS , 3 MASTERDRIVE and 3 Sinamics G120 .
2. At this time the selector of the PLC is in STOP .
3. In the Master Drive and Sinamics , I do a factory reset .
Step 4. Now the PLC from STOP to RUN .
5. The PLC must "parameterized" The drives.
6. The parameters DRIVES now have to put the PLC.
7. In conclusion drives the parameterized PLC ( without me connected to the PLC) at the first start of this .
I have attempted in different ways but failed some , still using the examples in the manuals coming , any idea ?
A PLC with Profibus is not the best tool to parametrize a Masterdrive. You can only use the Profibus PKW mechanism for one parameter at a time, which would make it very long and frustrating to setup all the required parameters. The adequate tool should be DriveMonitor. Try this download: DriveMonitor Version V5.5 SP2 for SIMOVERT MASTERDRIVES, MICROMASTER and SIMOREG. Hope this helps, Daniel Chartier
|
Last edited by: dchartier at: 5/11/2015 8:58:22 PMLast edited by: dchartier at: 5/11/2015 9:00:12 PM |
|
This contribution was helpful to1 thankful Users |