Dear dechartier In my case, I have an fdc107 6es71570ad820xa0, which I would like to link two PA flowmeter and a DP Profibus CPU with it. the problem is I'm not sure that I need a junction and terminator or I can couple those two flowmeters without any other stuff ?! I would like to wait for your helpful comments . Thank you ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/26/2019 08:40:42New subject after splitting |
|
8/26/2019 4:47 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685) |
Hello welfi; The following screenshot shpws you how Siemens proposes a number of PA instruments be connected to a FDC 157-0, using one or more AFD modules. The information was taken from this manual, which you should consult to setup your PA network properly: SIMATIC Bus links DP/PA coupler, active field distributors, DP/PA Link and Y Link https://support.industry.siemens.com/cs/us/en/view/1142696 As you can see a termination resistor is always necessary at the end of a PA segment. Siemens proposes this part number, to be associated with their Split-Connect technology for Profibus-PA cabling: SpliTConnect M12 Terminator: 6GK1905-0AE00 Another option we have used in certain projects, from MTL/Relcom, now a property of Eaton, uses Foundation Field bus Megablocks as field distributors, with an optional termination block. FF uses the same physical layer as Profibus-PA so the megablocks are compatible, and we have found the Megoablocks easier to wire than the Split-Connect system, and very reliable in our installations. https://www.relcominc.com/megablocks https://www.mtl-inst.com/images/uploads/INM_F300_Rev6.pdf Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 08/26/2019 16:48:45Last edited by: dchartier at: 08/26/2019 16:54:31Last edited by: dchartier at: 08/26/2019 17:29:42 |
|
Follow us on