5/20/2012 10:22 AM | |
Posts: 49 Rating: (1) |
Hi I am Facing Problem with 6RA70 it continously showing Alarm A083 .I Changed the Cable Still Fault is not reseted.
|
5/20/2012 11:09 AM | |
Posts: 49 Rating: (1) |
Dear Sir Drive is PLC controlled.Machine is Running Since 1 year.LED Status Red &Yellow is Glowing and Green is not Glowing.
|
5/20/2012 12:05 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Have you checked r650 bit 10 value? |
5/20/2012 1:01 PM | |
Posts: 49 Rating: (1) |
Dear Sir r650 bit 10 is high when There is no Alarm. At Time Of Alarm A083.we are not able see the status of this bit. |
5/20/2012 1:46 PM | |
Posts: 49 Rating: (1) |
Dear Sir We Changed The Cable with Terminals.We Can't see PLC programm and Drive Parameters as it is Locked By Some Other Person .
|
5/21/2012 7:51 AM | |
Posts: 49 Rating: (1) |
Dear Sir We Changed The CBP With New Card .Checked the screen ,replaced The Connectors.still Problem is as it is.
|
5/21/2012 8:08 AM | |
Joined: 8/25/2006 Last visit: 4/25/2024 Posts: 2203 Rating: (277) |
Hello. Please check drive parameters r063 and r064 for initialization and compatibility of CBP. Then you may check parameter n732.01-32 for CB diagnostics (description see in manual, chapter 7.7.2.2). Have somebody changed something in PLC? |
9/26/2015 10:03 AM | |
Posts: 1 Rating: (0) |
sir i am also facing problem in 6ra70 drive showing alarm A083 and A084.
|
9/3/2019 5:50 PM | |
Joined: 8/16/2015 Last visit: 5/3/2023 Posts: 31 Rating: (0) |
Yeah, did somebody make changes? 😌 Press Save, Download |