9/10/2018 8:11 AM | |
Joined: 1/2/2014 Last visit: 3/12/2024 Posts: 142 Rating: (22) |
Hello Sir, Our plant is running with S7 318 CPU and 5 ET200 M remote IO stations. We need to take out three signal modules[ 2 analog and one digital] which are configured already and existing in the station 2 and 4. Our plan is to use these cards in another system since they are basically idle [Configuraed hardware but not used in program or realworld]. We got three Dummy modules 6ES7370-0AA01-0AA0. how can switch it to dummy? 1. we like to do same with NO change in HW configuration in the program. is it possible to do plug and play? Link This link says for using a dummy in ET200M, Switch must be in NA position and Dummy is not configured, i.e. the modules are configured contiguously in STEP7 (HWConfig). Switch in NA position means original HW configuration must be edited by deleting the unwanted modules? We are confused. Please guide how can we replace with the dummy without changing HW The software is Simatic Manager |
Last edited by: RIAN Che at: 9/10/2018 8:16:58 AMLast edited by: Jen_Moderator at: 9/10/2018 1:41:41 PMOptimized link. |
|
9/12/2018 1:21 PM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hello, please go to Chapter 7.3 --> Table 7.2: Attachments7300_module_data_manual_en-US_en-US.pdf (166 Downloads) |
Last edited by: Jen_Moderator at: 9/13/2018 10:04:23 AMAdded file as an attachment. |
|
This contribution was helpful to2 thankful Users |
Follow us on